"What temperature have you set the HW to on the boiler? If it's set too low it's probably reaching it's temperature sooner and then flaming out before it kicks in again." I'll try and answer the other Q's on here as well. Set the hot water at 60 ish.. never seems to get therr.. If I run the central heating that runs fine only seems to be the water | |||
Reply privately | Reply in forum | Reply +quote |
"When was it last serviced? Heat exchanger could be blocked " Serviced about july this year, Its on a service contract so gets one every year, only thing the guy found was a leak on the expansion vessel which he reinflated | |||
Reply privately | Reply in forum | Reply +quote |
"When was it last serviced? Heat exchanger could be blocked " When it was installed they fitted a magnatite filter (fernox tf1) | |||
Reply privately | Reply in forum | Reply +quote |
"What temperature have you set the HW to on the boiler? If it's set too low it's probably reaching it's temperature sooner and then flaming out before it kicks in again. I'll try and answer the other Q's on here as well. Set the hot water at 60 ish.. never seems to get therr.. If I run the central heating that runs fine only seems to be the water " • It could be your flow switch. | |||
Reply privately | Reply in forum | Reply +quote |
| |||
Reply privately | Reply in forum | Reply +quote |
| |||
Reply privately | Reply in forum | Reply +quote |
"What temperature have you set the HW to on the boiler? If it's set too low it's probably reaching it's temperature sooner and then flaming out before it kicks in again. I'll try and answer the other Q's on here as well. Set the hot water at 60 ish.. never seems to get therr.. If I run the central heating that runs fine only seems to be the water • It could be your flow switch." I'll ring the serv8ce co. Tomorrow, was hoping for a quick fix or my shower in the morning wi be very brisk. | |||
Reply privately | Reply in forum | Reply +quote |
| |||
Reply privately | Reply in forum | Reply +quote |
| |||
Reply privately | Reply in forum | Reply +quote |
| |||
Reply privately | Reply in forum | Reply +quote |
| |||
Reply privately | Reply in forum | Reply +quote |
| |||
Reply privately | Reply in forum | Reply +quote |
| |||
Reply privately | Reply in forum | Reply +quote |
"My combi boiler seems to be playing up When I demand hot water I hear the boiler fire up then a short while later with the tap still running the burner stops if I leave the tap running it kicks in again then stops and so on. I've checked water pressure its about 1 1/4 bar, no error codes. Anything I might be able to do before I ring the boiler man ?" its diverter valve depending on your boilers make. If faulty it tends to heat a rad closest when it fires up a quick check will point this out. | |||